I have a R3 controller. All has worked fine for 2 months. Now on the last two scheduled cycles, I am getting low flow alerts when each zone either runs or finishes running.
I manually ran a few zones to confirm that water was flowing. The zones appear to run fine yet I still get the low flow alert. Before I recalibrate, I wanted to make sure there wasn’t anything else to look for.
I have seen that warning with some of my systems. They have usually resulted from a valve that failed to open such as a station valve or master valve. I would check the wiring for secure connections and check the Ohm reading on the individual coils.
I did have one other instance where a gopher bit into a wire causing the wire to only have a slight amount of copper left in it. The affected station would only work after previous stations had irrigated and cause the ground to get wet where the damaged wire was.
@franz, @emil
I just had this problem occur after i ran a successful calibration and the controllers starting their normal start times. I have three WFM’s and three master valves. I suspect the master valves. All three are acting this way. I did install bypass valves so that i may bypass the WFM’s. Any help from anyone would be appreciated.
Went out and ran several zones using quick run and watering took place.